Your Hydrominder could be bad. Just worked on one today for what might be your issue, the valve wasn't opening fully and was filling the tank so slow that it wouldn't create suction on the soap. A valve kit fixed it.
Well I wasn’t getting any pressure when the soap function was on. But I fixed thatThat video tells me nothing.
Measure across the two wires going to the coil. When you measure from hot to ground on the secondary side of a transformer you very well could be getting false readings.With a voltmeter, I have the function pressure on and I check the hot wire with one and I connect it to the nut which gives me a reading of 24 v
Yes, it's entirely possible you've lost the "common" connection back to the transformer in the cabinet. You can also check the solenoid with a screwdriver, when it's energized you'll feel a magnetic pull above the coil and a vibration that's the 60 hertz of the power.Measure across the two wires going to the coil. When you measure from hot to ground on the secondary side of a transformer you very well could be getting false readings.