I have a wash with 400 Watt Metal Halide lighting running off 230 Volts.
I want to convert one fixture at a time as they fail to CFL.
The new CFL lamp will fit in the fixture just fine, but it is a 120V lamp. I have two wires running to my fixture, both 120V to ground and 230/240 across them. If I were to convert all fixtures at one time I would just change one of the wires to neutral in the lighting panel or breaker box and wire directly to the lamp socket, but I can't do that if I change one fixture at a time.
Now my crazy idea:
The transformer in the 400 W Metal Halide fixture is a four tap (120V, 230V, 277V, and 460V). I want to toss the capacitor and keep the transformer. I want to rewire the transformer, use my existing incoming power to the fixture and transform it to 120V for the new CFL lamp. I don't know how (or even if possible) to rewire it because I don't know the designed output voltage of this transformer. If I had this designed output voltage I could figure if I could convert my incoming 230V to something close to 120V. As I typed this, I just realized I could get up on the ladder and just measure it - so that's what I'll do.
What do you think? Will it work?
I want to convert one fixture at a time as they fail to CFL.
The new CFL lamp will fit in the fixture just fine, but it is a 120V lamp. I have two wires running to my fixture, both 120V to ground and 230/240 across them. If I were to convert all fixtures at one time I would just change one of the wires to neutral in the lighting panel or breaker box and wire directly to the lamp socket, but I can't do that if I change one fixture at a time.
Now my crazy idea:
The transformer in the 400 W Metal Halide fixture is a four tap (120V, 230V, 277V, and 460V). I want to toss the capacitor and keep the transformer. I want to rewire the transformer, use my existing incoming power to the fixture and transform it to 120V for the new CFL lamp. I don't know how (or even if possible) to rewire it because I don't know the designed output voltage of this transformer. If I had this designed output voltage I could figure if I could convert my incoming 230V to something close to 120V. As I typed this, I just realized I could get up on the ladder and just measure it - so that's what I'll do.
What do you think? Will it work?