I had downloaded the pdf manual for my Dixmor, but of course I can't find it.

The temp. says -22 F. It's 28F outside.

Time for a new temp. sensor?
 

Jeff_L

Well-known member
Joined
Dec 27, 2007
Messages
1,246
Reaction score
31
Points
48
Location
Missouri
Could be, but also inspect the wire going from your WeepMizer to the temp sensor to make sure there are no breaks, exposed wire, etc., in it. I had a GoldLine thermostat reporting odd temps and found the wire to the RTD had rubbed on a metal corner for so long that it rubbed right through the insulation and was shorting on the metal and giving false readings.
 

cantbreak80

Maybe I need new clubs
Joined
Feb 10, 2008
Messages
1,126
Reaction score
574
Points
113
Location
CO
What Jeff said.

If it's not a connection or broken wire, order two sensors and install them both...in different locations. The WM will use the coldest of the two.
 

robblackburn

Member
Joined
Aug 31, 2007
Messages
146
Reaction score
0
Points
16
Location
Louisville, Ky.
Unit needs to be recalibrated

I had downloaded the pdf manual for my Dixmor, but of course I can't find it.

The temp. says -22 F. It's 28F outside.

Time for a new temp. sensor?
I just went thru the same thing. The temp sensors are most likely ok. The unit needs to be sent in for recalibration. This seems to happen to much with the Weep Mizer. The good thing is that it only costs around $25. Just give them a call and they will let you know.

Rob
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,862
Reaction score
1,370
Points
113
Location
Orange, MA
thanks everybody.

that's why i love this forum.

super!
 

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,668
Reaction score
1,982
Points
113
You most likely have a bad temperature sensor or cable since it's only about 2or 3 years old. I sent you the latest DX1000 manual.
 

Greg Pack

Wash Weenie
Joined
Sep 3, 2007
Messages
4,151
Reaction score
1,809
Points
113
Location
Hoover, Alabama
IIRC -22 is the default temp you will see when no temp sensor is connected. As Randy said, broken/rubbed wire or bad sensor is the most likely culprit.

Years ago I had a dixmor wire rubbed at a c-channel purlin on a metal roof. My guess the wind caused the roof to move enough to rub the wire.
 