Can I grab 24v from a bay transformer to power the weep miser or should I feed it with a separate power supply?
Years ago, I may have seen this somewhere, I started installing all solenoids with a power cord and plug for an outlet. The power source for that solenoid was then wired to an outlet. I did this because hard wired solenoids for the tunnels were a pain to change without killing the power and ran the risk of a short if i didn't and needed to do it fast and on the fly. Now I simply unplug it and swap it out and plug it in again.Its nice to have a switch disconnecting power to the solenoid like mentioned. I always test my weep when I know the temps are going to drop below freezing. It makes it easy to test when temps are above 36°. I had a weep gun malfunction once and didn't discover it untill the bay froze up. Then I installed the switch!
So 3 solenoids is a bit over 1 amp. Doesn't seem like much...but what does the 40va refer to on the supply transformer?A 24V solenoid pulls a lot of amps. One Dema NO solenoid is .4 amps at 24V.
It seems as though that rating (40va) is common with these off the shelf transformers and power supplies. Is the something more "robust" available?I had to research it - it wasn't as direct as I thought.
It goes vA ÷ V to get the amps the transformer can produce, so 40 vA ÷ 24 = 1.67A. Watts ÷ volts = amps, so 10 watts per solenoid ÷ 24 volts = .41 amps. That's assuming Dema NO solenoids - I've seen some, like ASCO, up to 22 watts.