Water seeping back into hp soap holding tank which dilute chemical mix. I don't see check valves on back side. I notice when I use rinse, it fill up more...but could be coincidence. Btw I already check hydrominder. Suggestions?
 
Last edited:

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
The check valve is in the bottom of the hot water tank. It's a 3/4" valve, there's not a separate one for soap or wax.
 

txheat

Member
Joined
May 12, 2010
Messages
277
Reaction score
1
Points
18
Location
texas
Thanks Mep...which one? Do they correspond to each chemical holding tank?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
There's one check valve for each bay, and one of them is likely bad. If you're still running hot water, the easiest way to find which one is bad is to run each bay on soap until the valve gets hot, then turn to rinse. The bad check valve will get cold.
 