The single unloader is set at 1600psi. When the customer lets go of the trigger the VFD maintains either 1000 or 1400 depending on the pressure selected by the customer. The motor runs at about 15hz or so when the trigger is released since the flow is restricted. The transducer detects the pressure and it is wired to the VFD. The pressure doesn't hit the unloader pressure.
I can't believe you still think the dump gun is a good idea. Do you not realize that using a dump gun with a VFD pump system that if the customer is not pulling the trigger the tire cleaner will be dumping on the ground at around 4 gallons per minute?mjwalsh said:We like the type of gun (Cat has a version) that unloads around the outside of the nozzle when trigger is released. That way we have zero concern about heat building up in our unloader-regulator bypass hose. Do you think there is any chance the VFD would work with well with that type of gun.
The single unloader is set at 1600psi. When the customer lets go of the trigger the VFD maintains either 1000 or 1400 depending on the pressure selected by the customer. The motor runs at about 15hz or so when the trigger is released since the flow is restricted. The transducer detects the pressure and it is wired to the VFD. The pressure doesn't hit the unloader pressure.
I've never had a capacitor fail and I'll bet it's because the vfds have a low duty cycle compared to the event you're talking about. VFD are popular in large buildings and run 24/7.
If you use a dump gun with a VFD and transducer the pressure drop would cause the motor and pump to run at full speed. I've never used a dump gun so I assuming that is the case.
The transducers we use are from www.transducersdirect.com and were a 0-2000psi 1/4" two wire 4-20 milli-amp.
That's exactly what it does. It's just like taking the tip out of the gun and pulling the trigger.thoffmanjr said:I'm assuming the dump gun opens up flow which would cause a huge pressure drop which would cause the speed to hit 60hz.
I think you're missing something too. It solves a problem of wanting lower pressure available to the customer by letting them vary it in a wasteful manner that can even be done with a standard trigger gun. The whole discussion started when someone wanted to REDUCE the use of their product and you suggested the dump gun which would only INCREASE the use. That complete lack of understanding of the particular issue shows a lack of logic in choosing to use dump guns in the bay at all.mjalsh said:I could be missing something ... but it seems like with programming the conditions of both the selection & the lessened pressure ma signal to the PLC could make it so a lower rpm could occur fast enough to avoid the unwanted 4 gpm that Mep referred to.
That complete lack of understanding of the particular issue shows a lack of logic in choosing to use dump guns in the bay at all.
When using a Single Hose or Single Hose VFD system, do the low pressure chemicals go into the pump at application strength or are they mixed at the pump head with fresh water and diluted there ?
Thanks
The pressure is controlled by the VFD based on FLOW. It ramps the pump speed up (increasing flow) until the desired pressure is met. Your dump gun doesn't allow "a bit more flow," it allows the full capacity of the pump to be dumped around the tip. That means the flow to achieve 50 PSI can never be met even with the pump running at full RPM. It's not an issue with your FloJet system because there's presumably a needle-valve adjustment in the room preventing more flow when the dump gun is opened. It is once again not relevant to this situation.mjwalsh said:it does appear that Tom gets the VFD-motor driven pump down to 50 psi for his unique flush approach.
The pressure is controlled by the VFD based on FLOW. It ramps the pump speed up (increasing flow) until the desired pressure is met. Your dump gun doesn't allow "a bit more flow," it allows the full capacity of the pump to be dumped around the tip. That means the flow to achieve 50 PSI can never be met even with the pump running at full RPM. It's not an issue with your FloJet system because there's presumably a needle-valve adjustment in the room preventing more flow when the dump gun is opened. It is once again not relevant to this situation.
You're mistaken. The transducer, along with the VFD, is also the pressure regulator. In order to make pressure, you need flow and a restriction. With a dump gun, rather than increasing the restriction when the trigger is released the restriction is reduced. The pump will speed up to try and achieve the pressure programmed into the controls.mjwalsh said:I believe Tom's approach is using a transducer for pressure monitoring mainly to allow for a slightly lower pressure as a choice.