IBA "Stop" Light blows bulbs

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,862
Reaction score
1,369
Points
113
Location
Orange, MA
I use the car type lamps for stop, enter, backup on my IBA.

The Stop light started blowing every once in awhile and now is blowing daily.

It really blows the bulb apart.

Trouble is I can't test the voltage at the wire because I need to start a wash to trigger the stop light and the gantry door/spray bar are in the way because of the proxes that need to be lit for the machine to say 'stop'.

Any ideas? Try replacing the cable end? Water getting in? Vibration? It just hates me???:rolleyes:
 

JIMT

Member
Joined
Sep 4, 2007
Messages
143
Reaction score
0
Points
16
Location
Toledo, Oh.
You should have an output on the PLC that you can jumper to turn the Stop light so you don't have to turn on the wash to check the voltage at the light.
JIMT
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
My first guess would be that the bulb is getting wet. The indicator should be the glass turning an opaque blue color.
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,862
Reaction score
1,369
Points
113
Location
Orange, MA
The bulb breaks all apart when it happens and the base glass that is left is a tan-ish color.
 