Here's my dumb question of the day. Somehow managed to own the car wash 5 years without having to deal with this. I had the gas was turned off for some remodeling and now I'm not sure how to get the thing lit back up.

It's a raypak. All I've ever done in the past is just flip the switch on the side of it to get it started (attached picture). Also attached a picture of the inside.

The directions on it say to close the gas valves, close the manual pilot valve, turn off power, open manual pilot valve, turn on power, turn on gas valves.

I tried to do that to the best my ability but it doesn't seem to be lit. Also tried to get it to go with a lighter but wasn't really sure where to put the lighter to get it to light up.. lol.

View attachment 1289 View attachment 1288
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,302
Reaction score
1,187
Points
113
Location
Ohio
It might take a few cycles to bleed out the air but there is no pilot for you to manually light.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
It looks like it's been converted to an electronic ignition. Just turn on all the valves and turn the power on. If you smell strong gas at any point, turn everything off and call a boiler expert.
 

Overachiever

Active member
Joined
Feb 26, 2014
Messages
338
Reaction score
84
Points
28
Location
IL
Thanks, I've tried flipping the switch several times and the only thing I notice that happens is the recirculating pump turns on. Is there somewhere specific I'm supposed to bleed air out of it, assuming that is the issue or will just keeping the power on it for a while be all I need to do?
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,302
Reaction score
1,187
Points
113
Location
Ohio
You should hear the igniter constantly clicking until fire.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
And if you don't hear the igniter clicking, your flow switch may be bad.
 

6t7gto

Member
Joined
Sep 10, 2007
Messages
254
Reaction score
18
Points
18
Location
bedford,ohio
I just had my raypak shut down on me.
It was a bad ground to the igniter down by the pilot.
I ran an additional ground wire from the bracket the holds the pilot/igniter back to the boiler cabinet.
david
 

Overachiever

Active member
Joined
Feb 26, 2014
Messages
338
Reaction score
84
Points
28
Location
IL
Thanks guys, I got it figured out a couple days ago, just in time for the big freeze. There is something on it that makes sure their is enough antifreeze in the system before it will try to start up and I guess I didn't have quite enough in there.

Also noticed the pressure relief valve had a plug in it, maybe the previous owner was trying to blow the place up, haha..
 

6t7gto

Member
Joined
Sep 10, 2007
Messages
254
Reaction score
18
Points
18
Location
bedford,ohio
I had that happen to me a long time ago.
The flow switch is located on the right side of my Raypack.
 