What's new

Help with Ginsan boards frying

slash007

Well-known member
Joined
Jul 8, 2012
Messages
2,405
Reaction score
322
Points
83
Location
Lexington, Ky.
I am trying to help a friend with his wash and we are trying to figure out why the boards in his SS Ginsan doors keep frying. Started about a month ago and happens randomly and to different bays. Any idea what could cause something like this? He's had several electricians try to figure out the issue and they don't see any voltage issues, but of course car wash experience is different. The electric company even replaced the transformer to the building and they noticed it had some minor regularities. Here is a picture of one door: Screensho.jpg

He's been sending them back to Ginsan and getting them repaired, but it keeps happening.
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
Not sure what we're looking at there, but I would start with an ammeter on the timed load and run each option and verify nothing is pulling more than 2 amps. Have these boards been installed on the same equipment for a long time?
 

slash007

Well-known member
Joined
Jul 8, 2012
Messages
2,405
Reaction score
322
Points
83
Location
Lexington, Ky.
Yes, same original equipment, nothing has been updated or changed. So just run each option and timed load should not be above 2 amps?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,933
Points
113
Location
Texas
It would help to know what that component is that keeps burning up. Does it happen again on a board that's been repaired? Could be something that's just failing with age.
 

Dan kamsickas

GinSan Technician
Joined
Aug 31, 2007
Messages
588
Reaction score
677
Points
93
Location
Grand Rapids, MI
That is a capacitor that helps regulate the incoming power supply to the board. That is what one looks like when the incoming voltage goes too high(over 30VAC +/-)
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,933
Points
113
Location
Texas
That is what one looks like when the incoming voltage goes too high(over 30VAC +/-)
Then assuming all the "commons" are connected together somewhere, I would recommend checking all the 24V outputs against each other. If you use a voltmeter and touch one probe to bay 1 "hot" and the other to bay 2 "hot," the voltage should be at zero; same with the commons. If someone has moved a wire while changing a transformer or contactor, you could be getting 48V between two bays. I always start at the contactor inputs and make sure they're in phase there (Same procedure as checking the transformer outputs), then make sure the transformers are all getting power from the same lines.
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
Based on Dan's component ID, I would consider what MEP said, and also verify that one of the 'electricians' didn't land a line wire somewhere like possibly on a contactor overload relay (electricians are used to doing that to break the control circuit). In that case, all would work fine until someone turned up the pressure too high on a bay, and when the overload tripped, 110V would ride the 24 Hot wire until the smoke leaked out. Are there individual transformers per bay? Who makes the pump stand?
 

mjwalsh

6 bay SS w/laundromat
Joined
Sep 7, 2007
Messages
3,131
Reaction score
172
Points
63
Location
North Dakota
I wonder if a "floating ground" might potentially have a way to contribute to an intermittent problem similar to this? My EE control specialist nephew tended to be a stickler for making sure that one side of the 24VAC was best always made to be 0 VAC.
 

slash007

Well-known member
Joined
Jul 8, 2012
Messages
2,405
Reaction score
322
Points
83
Location
Lexington, Ky.
Thanks guys. I just got involved trying to help, so will get as much information as possible. It is a Ginsan pump stand. Makes sense that power is sneaking in from somewhere. I wonder if he had electricians try to fix something in the past and they did it their way and created this mess.
 

mac

Well-known member
Joined
Sep 3, 2007
Messages
3,558
Reaction score
790
Points
113
I like Ginther's idea best. Have seen where a failing solenoid or contactor coil draws more amps than it should and makes things fail. Not enough amps to trip the circuit breaker. His way tp eliminate that is the best. Know how to use an ammeter and check every function. The use of regular electricians is mostly tricky at best. They can tell you what gauge wire to run to a circuit breaker, and what size breaker, but they are not trained in troubleshooting electronics. Another cause could be water. Many years ago all the meter boxes were wired so that if you squirted tire cleaner in the slot, the time would accumulate. Look for any signs of that. The fact that they are all now failing randomly may be a red herring. Have just seen too many things that happen for no traceable reason. Security cameras in the bays may help with vandals. I also doubt the analysis that now, all of a sudden, they are failing, when they have worked for years. Unless someone has cursed the place with bad juju, that don't fly. You could ask the power company to put on a recording device that monitors the line voltage. Most do it for free. These are all just stabs in the dark, but sometimes even a bling squirrel finds an acorn.
 

slash007

Well-known member
Joined
Jul 8, 2012
Messages
2,405
Reaction score
322
Points
83
Location
Lexington, Ky.
I think for sure that somehow double 24v is getting to the board, so starting there is a good idea. If it was only one bay, I would think that maybe 2 wires were somehow fused together somewhere on the way, but it affected all 4. From what I learned today, all 4 bays went out at different times during a 3 week period. They replaced the boards with a mix of rebuilt and new boards. So far 3 bays have already gone back down with the 4th still kicking. Out of the 3 that went down, 1 had a new board, 1 had a rebuilt board and the 3rd still has a working board, but no HP functions were working, so they kept it shut down until they could figure out what was going on so that that board wouldn't fry. I haven't been to the wash yet, but plan on going the first chance I get. They say nothing electrical was performed before the boards started acting up other than the utility company working in the area.
 

washnvac

Well-known member
Joined
Mar 30, 2008
Messages
1,033
Reaction score
157
Points
63
Location
Seaford, DE
I dumped those boards and went back to rotary switches on the location that had them. No more board issues. Electronics and moisture really do not get along, regardless of how well they are coated. (IMO)
 
Etowah

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
If the utility company had something wrong, you would have larger sparks than those board components. If main power from the building goes directly to the transformer for the bay, you are looking at a miswire situation. Someone may have landed a hot wire in the wrong spot there. I dislike individual transformer setups because a very small screwup can cause a very big problem and be difficult to sniff out. If you can't find it, it might be cheaper than burning man-hours on just buying a larger transformer that will run all the bays. You will need to individually fuse each bay, but then you eliminate most miswire issues that would cause this issue (unless of course someone landed a building line wire on the controls....)
 
Last edited:

slash007

Well-known member
Joined
Jul 8, 2012
Messages
2,405
Reaction score
322
Points
83
Location
Lexington, Ky.
I think the bays are already individually fused. I was told that on one of them they received a complaint that the door lost power. They replaced the fuse in the ER to that bay and then went to the bay and the door was smoking. Seems weird though that the fuse wouldn't have just burned a 2nd time.
 

2Biz

Thread Killer!
Joined
Nov 22, 2010
Messages
2,776
Reaction score
397
Points
83
Location
Ohio
I'm siding with Mep and JGinther on this one. Sounds like the transformers aren't phased correctly if commons are connected. Especially when you say they are down to 1 bay and it seems to be working correctly....Makes sense IF they have power turned off to the other affected bays...
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
I think the bays are already individually fused. I was told that on one of them they received a complaint that the door lost power. They replaced the fuse in the ER to that bay and then went to the bay and the door was smoking. Seems weird though that the fuse wouldn't have just burned a 2nd time.
They're individually fused, but probably on the transformer secondary. If you remove the transformer like I mentioned, you will also remove the fuses. That's why I said you would need to add them.

Burning up a component will only blow a fuse if it's pulling too many amps while doing so (shorting). The fuse doesn't care about the fire, only how much amps the wire is currently pulling and for how long.
 
Etowah
Top