I am an electrician by trade. Code requires a 12 gauge wire for a 5 hp 3 phase motor. I know of no benefit to using 10 gauge wire. (.63 versus .40 voltage drop that's 23 one hundredths of a volt less voltage drop for 10 gauge at 20 feet in length.) Code permits up to a 30 amp breaker but does not require it. (30 amp is allowed on 12 gauge wire for a motor load). I have 5 bays running on 20 amp breakers with 5 hp motors and 1200 psi. I don't remember the tip size but the motors pull about 8-9 amps. You are only using about 2.6 hp of the 5 hp motor anyway. Could have kept your old motors and saved a bit but oh well. gpm x psi then divide by 1460 for how many hp you need. Lots of misconceptions out there. As pointed out above 3 and 5 hp motors turn at the same speed and therefore pump the same amount of water. Buy a 500 foot roll of 12 gauge thhn wire at lowe's and tape the wires black red blue left to right and top to bottom. Run a fourth black wire and tape it green for grounding. (If you want to be technically right you need to buy a roll of green wire because you are not permitted to reidentify smaller than 6 gauge wire but it's the exact same product with a different color jacket so I would have a hard time spending another $50 for green instead of $2 for a roll of green tape.)
I am an electrician by trade. I have 5 bays running on 20 amp breakers with 5 hp motors and 1200 psi.
I am an electrician by trade. Code requires a 12 gauge wire for a 5 hp 3 phase motor. I know of no benefit to using 10 gauge wire. (.63 versus .40 voltage drop that's 23 one hundredths of a volt less voltage drop for 10 gauge at 20 feet in length.) Code permits up to a 30 amp breaker but does not require it. (30 amp is allowed on 12 gauge wire for a motor load). I have 5 bays running on 20 amp breakers with 5 hp motors and 1200 psi. I don't remember the tip size but the motors pull about 8-9 amps. You are only using about 2.6 hp of the 5 hp motor anyway. Could have kept your old motors and saved a bit but oh well. gpm x psi then divide by 1460 for how many hp you need. Lots of misconceptions out there. As pointed out above 3 and 5 hp motors turn at the same speed and therefore pump the same amount of water. Buy a 500 foot roll of 12 gauge thhn wire at lowe's and tape the wires black red blue left to right and top to bottom. Run a fourth black wire and tape it green for grounding. (If you want to be technically right you need to buy a roll of green wire because you are not permitted to reidentify smaller than 6 gauge wire but it's the exact same product with a different color jacket so I would have a hard time spending another $50 for green instead of $2 for a roll of green tape.)
Based on wash4me's above quote ... that (gpm x psi)/1460 is the limiting factor & it still does not tell us what the amps the specific motor draws when it first starts up. It seems like single phase is worse when it comes to the starting amp criteria creating the need to go to a higher amp breaker. As far as the breaker throwing ... I have read that some breakers & even between brands do not all have the same throw sensitivity. Older Federal breakers come to mind. Our friend Slash007 could be considering a Super Bay(s) with more pressure & volume if the pump part of the equation can handle it.
mike
Should I use stranded or solid wire for the pumps? Also, I have been going back and forth between using 10 and 12 gauge wire after your post. My cable run is only going to be 25' or less, so it seems that I can get away with a lower gauge wire.. Other than that, is there a limit to how many wires I can run in the conduit? I am going to have 26-28 wires total.
Should I use stranded or solid wire for the pumps? Also, I have been going back and forth between using 10 and 12 gauge wire after your post. My cable run is only going to be 25' or less, so it seems that I can get away with a lower gauge wire.. Other than that, is there a limit to how many wires I can run in the conduit? I am going to have 26-28 wires total.
Based on wash4me's above quote ... that (gpm x psi)/1460 is the limiting factor & it still does not tell us what the amps the specific motor draws when it first starts up. It seems like single phase is worse when it comes to the starting amp criteria creating the need to go to a higher amp breaker. As far as the breaker throwing ... I have read that some breakers & even between brands do not all have the same throw sensitivity. Older Federal breakers come to mind. Our friend Slash007 could be considering a Super Bay(s) with more pressure & volume if the pump part of the equation can handle it.
mike
Stranded wire is used for flexibility. Either one will do the job the same.
Here's a chart for number of wires in a conduit:
https://www.theautomationstore.com/maximum-number-of-conductors-in-conduit/
Thanks! I searched for something like that, but couldn't find it. I was worried about putting in too many wires in one conduit. I plan on using the flexible grey conduit, probably 3/4 inch. Looks like with THHN at 12 gauge, i can fit 18 wires, so maybe I'll just use two runs and put 14 in each if they fit.
wash4me, the wires used in my old stand won't work because they are too short and run way differently. It is a custom stand and the power runs to a box on the wall from the breakers, then splits out to each pump. It is also almost 40 years old, so replacing it is the way to go. I guess if I am going to stick with 20 amp breakers, then might as well use 12gauge as well.
Thanks.