Blowing fuses

Kool Wash

Member
Fellas what would cause the fuse the blow anytime someone selects tire cleaner in any of my 6 bays. I thought it was the motor so I changed it, not it. This is Coleman equipment and I'm stumped. Thx for any and all replies in advance.
 
which fuse is blowing? Is it the inline fuse on each individual bay?

Does your pump unit have the ids mx controllers on it?
 
75va<transformer ÷ 24v = 3.12 amp. x this by 1.67 (167%) <allowable % of over current = 5.21 amp. is it possible you need a larger fuse?
 