  • I have a IDX TIMER at411, model . I can confirm the swiper is still lit up with the rainbow colors. It will turn green when a card is swiped. The vacuum does not come on at all.
    I did verify the low voltage fuse is not blown. What is next ?
    D
    Dan kamsickas
    You need to check the output of the AT411. Measure across terminal 6 and 3 on the 411. You really need to post this in the thread you started, also. That way others can use the knowledge in the future.
    Hello Dan FatBoy 769 said you might have the answer to my question, (is possible to install a timer buzzer on a GS-7.) It is hook to the sensortron at the coin location
    D
    Dan kamsickas
    There isn't an output on the GS-7 for a buzzer. If you're thinking you want it to beep when coins are deposited, you cannot do that either. As a side note, the GS-7 has been obsolete for almost 20 years.