What's new

Sta-Rite Booster Pump Blows Fuses

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
I apply my IBA presoaks and foam polish w/a sta-rite booster pump at 125 psi.

I was blowing 20A slo-burn fuses once in awhile. Now they are blowing every few cars.

Why would a pump start frequently blowing fuses? TIA.
 

bigleo48

Active member
Joined
Sep 6, 2007
Messages
1,887
Reaction score
0
Points
36
Waxman,

I have a similar problem and it was due to my motor contactors. One phase wasn't always connecting properly (damaged contacts) and so it would cause the other phase to overload and pop the breaker.

Hope this helps...Big
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
Mine is Sta-Rite, Model # HP10C-02MS1. 3/4 hp. 115/230V. 11.56 amp.

Phase-1. 60 hz.:)
 

Jeff_L

Well-known member
Joined
Dec 27, 2007
Messages
1,246
Reaction score
31
Points
48
Location
Missouri
As BigLeo said, contactor would be my first guess. Second would be the motor itself, how old is it? Use your amp meter to check each leg while it's running to see how much each one is drawing.
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
4 years old. We plan to check the draw w/our meter.

Thanks!
 

ken-pro

Equipment Distributor
Joined
Aug 31, 2007
Messages
140
Reaction score
2
Points
16
Location
Kitchener, Ontario
Because this is a single phase motor the most likely problem is the starter plate / capacitor start circuit contained within the motor. The pump is likely drawing way too much power when it starts. You will likely find that the running amperage is fine.
 

Dean Taylor

Dean Taylor, CATEC.com
Joined
Sep 4, 2007
Messages
223
Reaction score
0
Points
16
Location
Sarasota, Florida
Kevin hit it on the head.

Your start up current is probably spiking above 20 amps. This typically happens only when the pump starts. You might try a 25 amp fuse. If it holds, then it is in fact your start-up current. You can also check it as suggested with an amp meter.

Might consider cleaning or replacing your contactor and possibly replacing the start-up capicitor.

Let us know what you find out.
 

bigleo48

Active member
Joined
Sep 6, 2007
Messages
1,887
Reaction score
0
Points
36
Waxman,

An amp clamp meter is a great tool to have and not that expensive. With all test equipment, you get what you pay for with regards to accuracy, but in the car wash environment, a $100 model would be able to tell you if you have a problem or not. You just clamp around the wire and read the current draw in amps.

Here's a website that seems to have the whole range. http://www.multimeterwarehouse.com/clampmeter.htm

Big
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
Thanks!

We tried w/my radioshack multimeter this am but couldn't figure it out. It does hold with a bigger fuse.
 

bigleo48

Active member
Joined
Sep 6, 2007
Messages
1,887
Reaction score
0
Points
36
Thanks!

We tried w/my radioshack multimeter this am but couldn't figure it out. It does hold with a bigger fuse.
Waxman,

Most multimeters have a 10A Max option. So too low in this instance, but in other instances, you need to change the leads so it's using the 10amp plug-in and put both leads in serial (as opposed to parallel when you take a voltage measurement). BTW, they usually have a separate fuse for the 10A next to the 9VDC battery. If that's blown, you won't be able to measure anything.

Need to get that amp clamp and find out what's going on. What size fuse are you using now? My guess is that the new fuse will only last so long until the problem gets worst and you may cause more damage.

Big
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
Called Sta Rite. They said it is likely the starter windings or main windings in motor itself. Their price was high so I ordered one from WW Grainger.

Thanks!
 

bigleo48

Active member
Joined
Sep 6, 2007
Messages
1,887
Reaction score
0
Points
36
Waxman,

So you're sure it's the pump? Have you had electrical problems that would cause pump damage? Maybe I'm wrong, but it sounds like you're changing it before you've clearly identified the fault. I would check voltage & amp draw at max pressure and make sure that the pump can make the specs listed and that it "sounds" ok (takes 2 minutes). Then I would try to find out why it happened so I didn't install a new pump just to damage it. You right...they are expensive :(

When you get the new pump, measure the coil resistance and cross-reference it with the one in service. Would be interesting to note.

Big
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
Big

It is the motor I have decided to spare part, not the pump. It's a c-face motor, 3/4 hp, 1 phaze etc.

Sta Rite has tech support and I talked it over with them before I chose to order one.

I asked about the returns policy if I am wrong (and they are wrong) in the diagnosis of this problem. It allows me wiggle room.

I have been burned this Winter in a rookie sort of way in not having ample spare parts or improper spare parts for my troubles.

The $280 (delivered) for this motor is to me cheap insurance and some peace of mind that I very much need right now. :eek:
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
Threaded motor shaft~how to couple to pump?

Tomorrow we'll be replacing the motor for my IBA's Sta- Rite boost pump.

Today we started looking at it to determine steps for removal/replacement.

I expected a spline on the motor shaft but instead found threads.

My original plan was to leave the pump in place and tear the motor off and replace. However, the threads have me wondering if I will need to un-plumb the pump and do the motor removal etc. on the work bench.

Anyone have experience in this area?

Thanks!:rolleyes:
 

ken-pro

Equipment Distributor
Joined
Aug 31, 2007
Messages
140
Reaction score
2
Points
16
Location
Kitchener, Ontario
Is this an impeller booster pump? (Pump itself is a long stainless steel cylinder). If so, then given the age you probably should just replace the whole pump. At 4 years old, and being disassembled you should be looking at replacing the impeller stack. I'm pretty sure if you add the price of the stack, mechanical seal, and the motor your are at or beyond the cost of a whole new pump. This style of pump can be tricky to rebuild given the number of pieces in the impeller stack. This is just my experience though.

No matter what, you will have to remove the whole motor pump assembly from the machine, and get it to a work bench to disassemble.
 

soapy

Senior Member
Joined
Sep 1, 2007
Messages
2,833
Reaction score
742
Points
113
Location
Rocky Mountains
Call Dan at Dultmeier and he can get you a replacement pump and motor. Give him the #s off the one you have and he can match it for you. I would also replace the whole thing and not just the motor in this situation. Somewhere in your town or close to it there should be a motor repair shop that could fix your motor or sell you a new one much cheaper than $280.
 

Wally

Member
Joined
Sep 9, 2007
Messages
176
Reaction score
0
Points
16
Location
Buford, GA
You can use the Grainger #2P019. I put one on a Laser last week. $450 total.
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
5,876
Reaction score
1,394
Points
113
Location
Orange, MA
Head Scratch Fix

Well.........

Tore pump and motor out of pump stand today.

Replacement motor was wrong part.

Took existing motor to a electric motor repair shop and it bench tested fine. Put strain on shaft, still fine etc. Checked amp draw at startup and run modes. Fine w/in factory specs.

Reassembled w/pump (impeller stack, mechanical seal, spring etc.). Fired back up and it runs fine now. Actually had about 15 more operating psi than before we tore it down. (?).

The internal parts looked fine; a bit rusty but otherwise fine.

Now I don't know what to do next.

Have a replacement setup like suggested on hand complete if problem comes back?

Have electrician test the complete circuit ?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
Did you ever test with an amp meter? You could have an issue with the wiring, and you'll never know if you don't do a load test on the motor.
 

pitzerwm

Active member
Joined
Aug 28, 2007
Messages
3,693
Reaction score
10
Points
36
Location
Tri-Cities, WA
A clamp on amp gauge is a must if you are dealing with any electrical appliances. You instantly know if AC power is flowing. And how much.
 
Top