What is the electrical requirement for a Laser dryer? I have 240v 3 phase at my wash, so anyone have the specs at that voltage? Need the breaker required and FLA on the motors.

thanks,
David
 

dreese

dreese
Joined
Sep 1, 2007
Messages
60
Reaction score
2
Points
8
LaserDri came in 2 models, each ran 2 motors. Circuits needed are:

30 hp - (1) @ 38 fla, (1) @ 41 fla @ 230VAC
40 hp - (1) @ 48.6 fla, (1) @ 53.2 fla @ 230VAC

Above ratings are load amps, does not include +25% service factor for breaker selection.

If you are looking at the MaxAir 2 circuits, each running (2) 7.5 HP motors, are used for the basic model (40 fla @ 230VAC each circuit). Add an additional circuit if side producers are used.
 
Last edited:

cherokee235

Member
Joined
Sep 9, 2007
Messages
154
Reaction score
0
Points
16
Location
San Antonio area
LaserDri came in 2 models, each ran 2 motors. Circuits needed are:

30 hp - (1) @ 38 fla, (1) @ 41 fla @ 230VAC
40 hp - (1) @ 48.6 fla, (1) @ 53.2 fla @ 230VAC

Above ratings are load amps, does not include +25% service factor for breaker selection.

If you are looking at the MaxAir 2 circuits, each running (2) 7.5 HP motors, are used for the basic model (40 fla @ 230VAC each circuit). Add an additional circuit if side producers are used.
So, at 30hp that would be 79 amps, right? A 100 amp breaker should get it.
I assume this is 240v 3 phase, correct?

David
 

dreese

dreese
Joined
Sep 1, 2007
Messages
60
Reaction score
2
Points
8
So, at 30hp that would be 79 amps, right? A 100 amp breaker should get it.
I assume this is 240v 3 phase, correct?

David
Yes, this is 230 / 240 VAC 3 Ph.
No, you need to run 2 separate circuits. The LaserDri (no longer in production) ran 2 motors, 15 or 20 HP each - thus the 30 or 40 HP designation. Most commonly used breaker for each circuit on the 208 VAC 30 HP dryer was a 60 amp. At 230/240, a case could be made to use 50 amp breakers, but I would check with your electrician.
If you are talking about the current dryer - the MaxAir - you still use 2 separate circuits. It was designed to be a drop-in replacement for the LaserDri using the same circuits. If side producers are added, an additional circuit is required.
 