I’ve got a vacuum that’s staying on and not shutting off. Anybody have any ideas? It’s a JE Adam’s 9213. I opened it up and found a wire that appears to be burnt. Everything else looks normal. As soon as I flip the breaker back on it starts running.
 

Attachments

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,668
Reaction score
1,982
Points
113
You've got a bad timer. Replace the timer and install a mercury relay between the timer and the vac motors to take the load off the timer.
 

Jim64

Active member
Joined
Sep 17, 2018
Messages
113
Reaction score
38
Points
28
Location
TN
I had a relay go bad in a fragra matic vac and caused the same issue
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
You can replace the relay module in those timers, but I haven't been able to find it at a reasonable price.

Adams doesn't do a very good job crimping the spades. That's why the wires burn. I usually rewire them with a 12 gauge going to the motors and really crush the hell out of the crimp. I feel like the 10 gauge just doesn't give enough to make a solid crimp connection.
 

Noob

Member
Joined
Oct 11, 2018
Messages
248
Reaction score
11
Points
18
Location
TN
It happened again. This time instead of staying on the vacuum simply won’t come on. Does anyone have any idea what causes this? MEP will running new wire prevent this happening?
 

Attachments

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,668
Reaction score
1,982
Points
113
It looks to me like you've got a bad timer. The reason it burned is there's to much load on the wire. If you install a mercury relay between the timer and the motors and have the timer control the mercury relay you wouldn't have this problem. The only load on the timer would be the coil of the relay, which is just about nothing. https://www.mdius.com/products/mercury-relay-35-amp-single-pole-120-vac-coil-normally-open-t-top we've been using these for well over 30 years, never had one fail. You can get them at kleen-rite
 

Noob

Member
Joined
Oct 11, 2018
Messages
248
Reaction score
11
Points
18
Location
TN
Thanks Randy,
I'll get a couple from KR and try and get them installed.
 

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,668
Reaction score
1,982
Points
113
The top terminal is your incoming power or line voltage, the next one down is the load, it goes to your vacuum. The 2 brass screw terminals are for the coil, connect the timed load from the timer to one of the terminals and common to the other. It's that simple. The relay has to be mounted straight up and down, just like you have it in your picture. Be sure to replace any wire that is questionable or burned.
 

Noob

Member
Joined
Oct 11, 2018
Messages
248
Reaction score
11
Points
18
Location
TN
One more questions guys. I ordered a replacement timer from KR and I’m thinking they sent me the wrong timer. The old timers look have something that looks like a bulb in the top right. The new one does not have that.
 

Attachments

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,668
Reaction score
1,982
Points
113
One more questions guys. I ordered a replacement timer from KR and I’m thinking they sent me the wrong timer. The old timers look have something that looks like a bulb in the top right. The new one does not have that.
That looks like it's a cap over the terminal. The timer looks to be correct
 

Noob

Member
Joined
Oct 11, 2018
Messages
248
Reaction score
11
Points
18
Location
TN
One last questions guys. Forgive me I don't have a lot of experience with electrical work. I just want to make sure I'm correct before I wire it up. Is my placement of the mercury terminal wiring correct? Also can someone tel me which 18ga black wire is the timed load?

Screen Shot 2021-08-20 at 10.46.33 AM.png
 
Last edited:

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
The two terminals on the right are input and load. You can use either one. Main power goes to one, load to the relay comes out the other. In your first diagram, the very top "10GA BLACK" on the barrier strip is the timed load out. See how it goes to the fuses and then the motors.
 

Noob

Member
Joined
Oct 11, 2018
Messages
248
Reaction score
11
Points
18
Location
TN
MEP what the easiest/correct way to connect the 10 ga wires to the mercury terminal blocks? It doesn't look like the holes are big enough to tie 2 wires together and insert them into the hole.
 

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,668
Reaction score
1,982
Points
113
When you get all done the timer will only control the coil on the relay, the coil only draws about 55 mA so the timer should last a lot longer. Think of the relay as a switch, you put power to the relay coil the coil energizes relay. The Load terminals are designed to take a 6-14 AWG wire. I connect the wires from the vac motors together and then connect the single #10 wire to the relay.
 