1 of my 4 bays is not getting power to the timer or coin acceptor. The bay without power in on a main circuit with another bay that does have power.

I am not strong at electrical troubleshooting, but I am guessing the issue is tied to the 24v transformer that feeds the timer & acceptor. My thought is to switch the transformer with another bay and see if the problem follows the tranformer.

I would like some tips from someone wiser before I pull the transformer. What is the smarter way to do this?

btw, I have checked the obvious stuff like breakers, fuses, and loose wires.
 
Joined
Nov 9, 2007
Messages
330
Reaction score
1
Points
16
Location
CT.
1 of my 4 bays is not getting power to the timer or coin acceptor. The bay without power in on a main circuit with another bay that does have power.

I am not strong at electrical troubleshooting, but I am guessing the issue is tied to the 24v transformer that feeds the timer & acceptor. My thought is to switch the transformer with another bay and see if the problem follows the tranformer.

I would like some tips from someone wiser before I pull the transformer. What is the smarter way to do this?

btw, I have checked the obvious stuff like breakers, fuses, and loose wires.
Have you checked to see if you have 24V out in the bay or in the controll box in the equipment room
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
You'll diagnose your problem a lot faster with a voltmeter than with swapping parts.
 

mjwalsh

6 bay SS w/laundromat
Joined
Sep 7, 2007
Messages
3,133
Reaction score
172
Points
63
Location
North Dakota
1 of my 4 bays is not getting power to the timer or coin acceptor. The bay without power in on a main circuit with another bay that does have power.

I am not strong at electrical troubleshooting, but I am guessing the issue is tied to the 24v transformer that feeds the timer & acceptor. My thought is to switch the transformer with another bay and see if the problem follows the tranformer.

I would like some tips from someone wiser before I pull the transformer. What is the smarter way to do this?

btw, I have checked the obvious stuff like breakers, fuses, and loose wires.
Tpoppa,

A 24vac non contact low voltage voltprobe is not as good as a full fledged multimeter but non contact voltprobe can be of value checking at what point you are loosing your voltage.

mike
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,667
Reaction score
3,937
Points
113
Location
Texas
Where would one find a 24v non-contact voltprobe?

The only time it would me MORE useful than a voltmeter is when searching along a wire for a break that for some reason isn't visible.
 

mjwalsh

6 bay SS w/laundromat
Joined
Sep 7, 2007
Messages
3,133
Reaction score
172
Points
63
Location
North Dakota
Where would one find a 24v non-contact voltprobe?
Tpoppa, Mep, & others,

http://www.all-spec.com/products/GT-16.html

http://www.greenlee.com/products/DE...0dADJUSTABLE-(GT%40d16).html?product_id=17647

There is a need to make sure the AC Voltage Hot wire is not too close to other wires when using a non contact device similar to this for the single probe to sense properly.

The value in using the non contact in my opinion is mainly just for a slightly quicker verification of a "no voltage" condition. Logically, from that you can determine ... if all the components are getting curent on the secondary (low voltage side) of the transformer. Or even to the transformer itself. I find there are times where it saves times verses getting out my trusty Fluke 12 multimeter.

Another plus: Less worry of accidently shorting the circuit with the metal probes of a multimeter. The single probe on the suggested non contact tester is insulated.

mike walsh king koin of bismarck
 
Last edited:

2Biz

Thread Killer!
Joined
Nov 22, 2010
Messages
2,785
Reaction score
404
Points
83
Location
Ohio
btw, I have checked the obvious stuff like breakers, fuses, and loose wires.
If you checked the fuse mounted to the transformer, how did you check it?
 
Last edited:

Tpoppa

Member
Joined
Dec 30, 2008
Messages
143
Reaction score
0
Points
16
Location
Ohio
If you checked the fuse mounted to the transformer, how did you check it?
I pulled the fuse on the transformer & visually checked it. I re-used the same fuse...for some reason it works now. Dirty contacts? Maybe the transformer is on it's way out?..not really sure.
 

2Biz

Thread Killer!
Joined
Nov 22, 2010
Messages
2,785
Reaction score
404
Points
83
Location
Ohio
I pulled the fuse on the transformer & visually checked it. I re-used the same fuse...for some reason it works now. Dirty contacts? Maybe the transformer is on it's way out?..not really sure.
The fuses on my transformers are sealed and the only way to check them is with an Ohm Meter. Thats why I asked since you stated you wern't strong at electrical troubleshooting. Still wondering how you knew the fuse was good by looking at it. Maybe yours is different than mine.

Mine are like this:

http://www.alliedelec.com/search/productdetail.aspx?SKU=70150946

I'm glad its working for you now....Although, You really need to know how to check the Primary and Secondary voltage of your transformer or find somebody that can help you. This is the only way to know whether it is good or bad or where the problem is.
 