Based on a career worth of experience with RO membranes, I think your concern re over pressurizing membranes is misplaced. Maximum pressure always far exceeds test pressure. If you run below test pressure, you will reduce the gals per day of purified water produced, and you will (potentially...
Agreed... and one thing to add. This is rarely done, and it should be done all the time. Have your plumbers add sufficient unions such that the softener and carbon tank valves can be disconnected from the plumbing with sufficient clearance that the valves can be unscrewed from their tanks...
If a membrane manufacturer does not provide the pressure spec... do not buy the membrane.
Can't say, that after 25 yrs of doing this, I've ever seen a max pressure that wasn't well above the test pressure/pressure spec. I wouldn't consider buying a membrane if the test pressure approximated...
The devil is in the details here. What is your pump output pressure? What membranes are installed?
When a manufacturer provides a temperature and pressure spec on a given membrane, nothing says those conditions are "ideal." They are just the conditions provided to the membrane during...
The two primary specs you want to match up are diameter and length which you've already done (4" x 40" nominal) and the pressure at which you run the system. For instance, we stock membranes with pressure specs @ 80 psi, 100 psi, 150 psi, and 225 psi...
We've seen issues with higher than expected water bills at customer's locations when water treatment equipment (e.g., backwashing carbon tanks, softeners, spot free RO systems) malfunction and run water to drain 24/7. Routine maintenance on the equipment solves the issue.
If needed, take a look at the label on the solenoid to determine the voltage it runs on. Might be 110vAC, might be 220vAC, or might be something less like 24 vAC.
Next, let us know the female thread size - often 3/4" or 1" are the more common sizes of RO's used in carwashes.
Let us know at...
No - it should not be doing that.
When commercial RO systems are "off" the current to the system is off. Without current, the normally closed solenoid valve at the inlet to the system should be closed. Yours isn't closing. Either take the solenoid valve apart and clean it (sometimes debris...
Typically the pipe that feeds the repressurization pump comes out of a bulkhead fitting installed near the bottom of a holding tank. The only pressure in that pipe is the head pressure from the tank (just a few psi - about 2.3 psi per foot of tank height). It would be unusual to have a...
Just noticed another thing in your pics. Someone has used a large set of channel locks to loosen/tighten your blue sediment filter housing. Bad practice. We have wrenches specifically for that purpose that do not damage the housing. remove, clean, and lube (food grade silicone grease) the...
That's a non-adjustable Series 6 pump, and I don't see a downstream valve - so I think what you get out of that pump is what you get. Your 225 psi membranes are not a good fit for your system. You need membranes spec'd at a lower pressure.
But the pump output isn't at the pressure you need. The pump should be fine once you get membranes installed that are a better fit for the system.
Don't close off the concentrate in order to get more pressure. Leave the concentrate at no less than 3 gpm.
Can you send some pics of your pump?
Nice! I'd turn that recycle up to 3 and recycle down to 1.5.
Is there a globe valve right after the pump or some other valve where you can increase the pump pressure? If not, you don't have enough pump to crank out the 225 spec pressure. When you're ready for new membranes we can look at...
So I should up pressure and try to get close to 225psi/4.8gppm while keeping reject flow at 3gpm?
Yes.
I can't advise you on the recycle issue unless you can give me the results of a lab analysis of the water. But, if it is city water, and you have appropriate pretreatment - meaning the...